Thank you for your question.

 The Vaisala WAA151 is compatible: 

To connect this sensor to the Symphonie Plus 3 you will
have to use one of the Flex channels 4-6 with a Digital Anemometer SCM (3151)



If you are powering the sensor for the heater you
should only have to wire the B-Ground to GND and C- front signal output to SIG.



If you are going to power the sensor from the iPack
battery, not including the heater power, you will attach the A- F+ power input
to EXC.

This is right on the boarder of being possible so I would
recommend two 5W PV panels instead of one.

 

The WAV151 Sensor is not compatible with the Symphonie Plus 3 logger because it has a gray code output.

 

Let me know if you have further questions.

Link to sensor:











http://www.vaisala.com/Vaisala%20Documents/User%20Guides%20and%20Quick%20Ref%20Guides/WAA151_User_Guide_in_English.pdf