rggovani Posted June 26, 2013 Report Share Posted June 26, 2013 I am very new to both NRG 200P and campbell CR1000 I am trying to connect NRG 200P to CR1000, I wrote a program to connect CR1000 to NRG200P ( i just dont quite know if it works yet). But i am having trouble wiring the 200P to the CR1000. The program that comes with CR1000 says that i need to connect Signal to 1H, Ground to ground, and power to VX1 or EX1. But i dont know what is Signal, ground or power. Link to comment Share on other sites More sharing options...
David Carlson Posted July 1, 2013 Report Share Posted July 1, 2013 I've attached a document that goes over the operation of the 200P and typical interface circuits. Basically, it's a 10K potentiometer. Give it a regulated voltage (less than 15V DC) at one end, ground at the other, and measure the ratiometric output voltage at the wiper . I hope that helps. anvanein.pdf Link to comment Share on other sites More sharing options...
rggovani Posted July 1, 2013 Author Report Share Posted July 1, 2013 So the data is collected from the Red end and the ground? I have attached two pictures, one the CR1000 input connections and second one of a screenshot of what the software (Short Cut) is telling me to do. It would be really nice if you could tell me where i should connect the Red (+), White (-), and Black (Ground) ends from my 200P Vane. -Thank You Link to comment Share on other sites More sharing options...
rggovani Posted July 1, 2013 Author Report Share Posted July 1, 2013 Software instructions Link to comment Share on other sites More sharing options...
David Carlson Posted July 2, 2013 Report Share Posted July 2, 2013 Hi, 200P (+) terminal --> Excitation, or VX1/EX1 (-) terminal --> Ground (Sig) terminal --> Signal, or 1H Does that help? Link to comment Share on other sites More sharing options...
rggovani Posted July 2, 2013 Author Report Share Posted July 2, 2013 Yes thanks that did help. But i dont think the numbers I am getting (from the datalogging software, PC200W) are right. I tried to Spin the NRG 200P Clockwise and the values goes from 0 to 90 degress at 90 degrees of NRG 200P , then to 70 at 180 degrees, and then 55 at 270 degrees. I also tied to change up the wiring a little, i had the (+) end at VX1, (-) end at H1 and Ground at Ground. I got different results this way, but looking at the values again from the data logging software and comparing it to real time (visually) they dont line up. Do do think there is something wrong with my programming or something wrong with the NRG200P? Link to comment Share on other sites More sharing options...
David Carlson Posted July 8, 2013 Report Share Posted July 8, 2013 Sorry for the delay; I've been out for the US July 4 holiday. You can test the sensor by following the instructions here: http://www.nrgsystems.com/TechSupport/KnowledgeBase.aspx?id=2&category=16 If it tests OK then you'll want to take another look at the programming. Link to comment Share on other sites More sharing options...